Had exactly the same issue doing exactly the same thing for the summer case. I don't know any way to suppress warnings. Obviously, the amount of heat exchange at the enthalpy wheel reduces to very small amounts when the flow from exhaust is <50% the supply side. It seemed as if the wheel stopped working, when I watched the outputs, but I actually have no idea how the object is programmed to react in these conditions. PS in the project I was simulating, an evapourative cooler was cooling the exhaust air (but making very moist) before the heatwheel to increase (take advantage) the sensible heat transfer (which is at about 70%, while the latent eff is only 30% therefore not missing much by "humidifying" the air).
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jason Kirkpatrick <jason.alan.kirkpatrick@...> wrote:
>
> All,
>
> I have a model including demand controlled ventilation and an enthalpy
> wheel treating the ventilation before the AHU. This all works ok, but since
> the ventilation is varying with the occupancy, the enthalpy wheel gives an
> error that the ventilation flowrate is too far from the design flowrate:
>
> ************* ** Warning ** HeatExchanger:AirToAir:SensibleAndLatent
> "F1:AHU HEAT RECOVERY": Average air volume flow rate is <50% or >130%
> warning continues. Air flow rate ratio statistics follow.
>
> I am wondering if there is a way that anyone knows of circumventing this
> warning or at least suppressing it.
>
> Thanks,
>
> Jason
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/