So what happens currently when the bounds are exceeded?
Does the wheel turn off? I could live with that.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> This issue has come up many times in the past. The
manufacturer cannot
> guaranteethe ratings of the HX when the flow rate
ratio is <50% or >130%
> of design. It's as simple as that. And there was no
guidance of what to
> do inside the model when the air flow ratio was out
of bounds since even
> the manufacturer could not tell us. If you want to
use this HX model,
> keep the air flow ratio within the boundaries of
where the model is
> valid. Otherwise, change to a flat plate HX (no
latent heat transfer).
>
> On 11/1/2011 4:04 PM, Jean marais wrote:
> >
> > Had exactly the same issue doing exactly the
same thing for the summer
> > case. I don't know any way to suppress warnings.
Obviously, the amount
> > of heat exchange at the enthalpy wheel reduces
to very small amounts
> > when the flow from exhaust is <50% the supply
side. It seemed as if
> > the wheel stopped working, when I watched the
outputs, but I actually
> > have no idea how the object is programmed to
react in these
> > conditions. PS in the project I was simulating,
an evapourative cooler
> > was cooling the exhaust air (but making very
moist) before the
> > heatwheel to increase (take advantage) the
sensible heat transfer
> > (which is at about 70%, while the latent eff is
only 30% therefore not
> > missing much by "humidifying" the air).
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>, Jason
Kirkpatrick
> > <jason.alan.kirkpatrick@> wrote:
> > >
> > > All,
> > >
> > > I have a model including demand controlled
ventilation and an enthalpy
> > > wheel treating the ventilation before the
AHU. This all works ok,
> > but since
> > > the ventilation is varying with the
occupancy, the enthalpy wheel
> > gives an
> > > error that the ventilation flowrate is too
far from the design flowrate:
> > >
> > > ************* ** Warning **
HeatExchanger:AirToAir:SensibleAndLatent
> > > "F1:AHU HEAT RECOVERY": Average air volume
flow rate is <50% or >130%
> > > warning continues. Air flow rate ratio
statistics follow.
> > >
> > > I am wondering if there is a way that
anyone knows of circumventing this
> > > warning or at least suppressing it.
> > >
> > > Thanks,
> > >
> > > Jason
> > >
> >
> >
>
> --