Very helpful, Brent. Thanks! I’ve had the same issue and was not sure what happened for the out-of-bounds periods. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Griffith, Brent If you want to ignore the warnings and run HeatExchanger:AirToAir:SensibleAndLatent outside of the approved range, then it is important to input the same effectiveness values at 75% and 100% flow. Those values create a linear model for effectiveness vs. flow and it can easily be the case that out-of-range flows produce nonsense effectiveness values. You need a flat, or at least very shallow, slope for that linear model and setting the effectiveness values to be the same at 75% and 100% does that. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jean marais Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.