[EnergyPlus_Support] Re: Water/Water HX ~ WaterHeater:Mixed



Okay, I got this working. The waterheater:mixed object sits on the demand side of the "primary" (first) Plant Loop and on the supply side "boiler branch" of the "secondary" (second) Plant Loop who's demand side consists of the "lower temperature" consumers.

So it works. It just doesn't work well when combined with a normal HVAC heating system. Although I've listed the radiant floor system as priority 1 in the zone equipment list followed by the ATUs on priority 2, the HVAC is doing all the heating and the radiant floor sees it's setpoint as met and therefore does nothing. 


My Zone heating setpoint is 21°C.
I've tried setting the radiant system setpoint at 21.6 with a 0.5 deg Throttling range(minimum) to force it to heat all the time, but this has no result. The economizer works between 21 and 24 Outdoor Drybulb...these are also my heating and cooling temperature setpoints.

The economizer high limit is set by ASHRAE. the rest is flexible. Any ideas?



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/