[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Dual Setpoint Error





copy the 2 schedules (cooling and heating set point temperatures) from your input file into the email so we can see them

On 11/4/2011 1:16 PM, Amruta Khanolkar wrote:
 
I did not make any changes in the heating setpoint schedule. I just increased the cooling setpoint schedule. So all the cooling setpoints in my new schedule are higher than the heating setpoints still it is giving me this error message,
"DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point".
 
Please help.
 
Thanks,
Amruta
 
 
 
On Fri, Nov 4, 2011 at 6:07 AM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
 

You increased the heating set point above the cooling set point. The cooling set point must be higher than the heating set point. Raise both temperatures.



On 11/4/2011 2:40 AM, ask_ami wrote:
 

Hi All,

I am working on a DOE prototype building(medium office). I created a new cooling set point schedule and assigned it at Thermostatsetpoint:DualSetpoint. In the new schedule I have just increased the set point temperature in stepped pattern by total 3.3 deg. C for 3 peak hous for a peak summer day. Remaining schedule is not changed. I am running this simulation for just that peak day. But after this change I got a severe error and my simulation terminated. The error is:
-------
** Severe ** DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point - increase deadband if using unmixed air model
** ~~~ ** occurs in Zone=CORE_BOTTOM During Warmup, Environment=Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, at Simulation time=06/28 00:00 - 00:10
** ~~~ ** LoadToHeatingSetPoint=-41431.055, LoadToCoolingSetPoint=-125592.948
** ~~~ ** Zone TempDepZnLd=429.02
** ~~~ ** Zone TempIndZnLd=11375.49
** ~~~ ** Zone ThermostatSetPoint=0.00
** ~~~ ** Zone HeatingSetPointOffset=0.00
** ~~~ ** Zone CoolingSetPointOffset=0.00
** Fatal ** Program terminates due to above conditions.
-------
Can somebody please explain me where did I go wrong?
Thanks,
Amruta


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___