You increased the heating set point above the cooling set point. The cooling set point must be higher than the heating set point. Raise both temperatures.
On 11/4/2011 2:40 AM, ask_ami wrote:Hi All,
I am working on a DOE prototype building(medium office). I created a new cooling set point schedule and assigned it at Thermostatsetpoint:DualSetpoint. In the new schedule I have just increased the set point temperature in stepped pattern by total 3.3 deg. C for 3 peak hous for a peak summer day. Remaining schedule is not changed. I am running this simulation for just that peak day. But after this change I got a severe error and my simulation terminated. The error is:
-------
** Severe ** DualSetPointWithDeadBand: Effective heating set-point higher than effective cooling set-point - increase deadband if using unmixed air model
** ~~~ ** occurs in Zone=CORE_BOTTOM During Warmup, Environment=Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, at Simulation time=06/28 00:00 - 00:10
** ~~~ ** LoadToHeatingSetPoint=-41431.055, LoadToCoolingSetPoint=-125592.948
** ~~~ ** Zone TempDepZnLd=429.02
** ~~~ ** Zone TempIndZnLd=11375.49
** ~~~ ** Zone ThermostatSetPoint=0.00
** ~~~ ** Zone HeatingSetPointOffset=0.00
** ~~~ ** Zone CoolingSetPointOffset=0.00
** Fatal ** Program terminates due to above conditions.
-------
Can somebody please explain me where did I go wrong?
Thanks,
Amruta
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___
- Follow-Ups:
- Re: [EnergyPlus_Support] Dual Setpoint Error
- From: Richard Raustad
- References:
- [EnergyPlus_Support] Dual Setpoint Error
- From: ask_ami
- Re: [EnergyPlus_Support] Dual Setpoint Error
- From: Richard Raustad
- Prev by Date: Re: [EnergyPlus_Support] Window wall ratio
- Next by Date: Re: [EnergyPlus_Support] Dual Setpoint Error
- Previous by thread: Re: [EnergyPlus_Support] Dual Setpoint Error
- Next by thread: Re: [EnergyPlus_Support] Dual Setpoint Error
- Index(es):