You should be using a Dual Set Point Thermostat and a separate SetpointManager for each coil. SetpointManager:SingleZone:Cooling for CC and SetpointManager:SingleZone:Heating for HC (or could use SetpointManager:MultiZone:Cooling;Average and SetpointManager:MultiZone:Heating;Average). If you have a draw through fan, you will need to store these SP's at nodes other than the CC/HC outlet node, and use a SetpointManager:MixedAir object to recalculate a new set point including fan heat and place these new SP's at the outlet of the CC and HC. On 11/10/2011 10:22 AM, ntraughpee wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.