[EnergyPlus_Support] Re: Heating/Setpoint Controller



All of this would need to be done in the expidf and not using the HVACTemplates, correct?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> You should be using a Dual Set Point Thermostat and a separate 
> SetpointManager for each coil. SetpointManager:SingleZone:Cooling for CC 
> and SetpointManager:SingleZone:Heating for HC (or could use 
> SetpointManager:MultiZone:Cooling;Average and 
> SetpointManager:MultiZone:Heating;Average). If you have a draw through 
> fan, you will need to store these SP's at nodes other than the CC/HC 
> outlet node, and use a SetpointManager:MixedAir object to recalculate a 
> new set point including fan heat and place these new SP's at the outlet 
> of the CC and HC.
> 
> On 11/10/2011 10:22 AM, ntraughpee wrote:
> >
> > PS: As I read it I was understanding that by using the 
> > HVACTemplate:System:VAV and having no availability schedule for either 
> > the HC/CC it would always be available when needed. Then I added in a 
> > constant set point, however from looking at the node temperature 
> > points in Results Viewer it is obvious that the HC/CC are operating 
> > year long at a constant set point.
> >
> > The system itself should be putting out like 55 degree air in max 
> > cooling, and 100 degree air for max heating. I have been trying to use 
> > the OA Temperature reset but again the coils seem to never shut down.
> >
> > What am I missing?
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, "ntraughpee" 
> > <matthew.sverre.anderson@> wrote:
> > >
> > > Hello Everybody, I have a question that likely (or at least 
> > hopefully!) has an easy answer and I am simply too foolish to know it.
> > >
> > > So I have a building which I modeled as a VAV with no reheat, and no 
> > preheat coil. I want the coils to operate as needed and simply ignore 
> > any frost warnings. However, I currently have no schedule for either 
> > since there will be many times during the fall/spring where we might 
> > need to heat/cool during the same day or during the week.
> > >
> > > The problem I am currently having is that the heating/cooling coils 
> > are operating year long at the same time. I want the HC to operate 
> > when the building needs heating, the CC to operate when the building 
> > needs cooling (neither to operate at the same time). Am I thinking 
> > about this incorrectly?
> > >
> > > Also is there a way to implement a dead band above/below the set 
> > point where the system is "satisfied" to prevent the system from 
> > "slamming" on/off?
> > >
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/