Can you have a look whether you can modify the CBVAV to work with a variable fan. I find that the problem user are having with VAV without reheat is that the variable fan without a bypass of the return air to the OA mixer cannot keep the reference node temperature steady while the fan speed is waiting for the zone damper to move. Without increase the fan flow volume the return air cannot be cooled to the reference node set point temperature. With the bypass path, the return air can be recycled through the cooling coil and be cooled independent of the zone air flow rate. ======================= Setting the reference temperature at the zone setpoint temperature would drive all the dampers to fully open. Setting the reference lower, would over cool. Without the reheat, the zone thormstat must be set to zero as minimum. Then the zone temperature will just float to the low set point temperature. When all the zones are below the zone setpoint, then the cooling is shut off. I am still experimenting with different conditions, because I do not know how the program is coded. I am trying to observe the system node conditions with different external and internal load level to find the program algorithm. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: RRaustad@xxxxxxxxxxxx Date: Thu, 10 Nov 2011 10:50:07 -0500 Subject: Re: [EnergyPlus_Support] Problem with results of a simulation
You are seeing the energy required to pull the zone temperature from
setback to setup temp. The ideal loads air system provides the
energy instantaneously. This is why you see the heating peaks.
Increase the setback temperature in heating mode to reduce the peak.
In V7, the ideal loads air system will have a maximum
cooling/heating capacity input to better model correctly sized
systems.
On 11/10/2011 9:34 AM, Ignacio wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |