All of this would need to be done in the expidf and not
using the HVACTemplates, correct?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> You should be using a Dual Set Point Thermostat and a
separate
> SetpointManager for each coil.
SetpointManager:SingleZone:Cooling for CC
> and SetpointManager:SingleZone:Heating for HC (or
could use
> SetpointManager:MultiZone:Cooling;Average and
> SetpointManager:MultiZone:Heating;Average). If you
have a draw through
> fan, you will need to store these SP's at nodes other
than the CC/HC
> outlet node, and use a SetpointManager:MixedAir
object to recalculate a
> new set point including fan heat and place these new
SP's at the outlet
> of the CC and HC.
>
> On 11/10/2011 10:22 AM, ntraughpee wrote:
> >
> > PS: As I read it I was understanding that by
using the
> > HVACTemplate:System:VAV and having no
availability schedule for either
> > the HC/CC it would always be available when
needed. Then I added in a
> > constant set point, however from looking at the
node temperature
> > points in Results Viewer it is obvious that the
HC/CC are operating
> > year long at a constant set point.
> >
> > The system itself should be putting out like 55
degree air in max
> > cooling, and 100 degree air for max heating. I
have been trying to use
> > the OA Temperature reset but again the coils
seem to never shut down.
> >
> > What am I missing?
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>,
"ntraughpee"
> > <matthew.sverre.anderson@> wrote:
> > >
> > > Hello Everybody, I have a question that
likely (or at least
> > hopefully!) has an easy answer and I am simply
too foolish to know it.
> > >
> > > So I have a building which I modeled as a
VAV with no reheat, and no
> > preheat coil. I want the coils to operate as
needed and simply ignore
> > any frost warnings. However, I currently have no
schedule for either
> > since there will be many times during the
fall/spring where we might
> > need to heat/cool during the same day or during
the week.
> > >
> > > The problem I am currently having is that
the heating/cooling coils
> > are operating year long at the same time. I want
the HC to operate
> > when the building needs heating, the CC to
operate when the building
> > needs cooling (neither to operate at the same
time). Am I thinking
> > about this incorrectly?
> > >
> > > Also is there a way to implement a dead
band above/below the set
> > point where the system is "satisfied" to prevent
the system from
> > "slamming" on/off?
> > >
> >
> >
>
> --
> Richard A. Raustad