[EnergyPlus_Support] Re: Air Flow Mixing



I would define a second zone. In this zone you must define the moisture and heat loads with a "OtherEquipment" object. How you ventilate it I leave you to decide, but I would use a simple ventilation object.

Then I would mix the airflow into your main zone using a "ZoneMixing" object. Be aware that the air flows must balance, else a (many) warning(s) result(s). If mixing occurs both ways, you'll need two zonemixing objects.



------------------------------------