Yes you can do that. But what you need to remember is that the HVACTemplate objects create many other necessary objects required for the simulation. Examples are the thermostat, zone equipment connections, schedules, etc. So the best way to do this is to run the HVACTemplate file and then work from the expanded file (*.expidf) to add your other ZoneHVAC equipment objects. You will need to modify some of the objects that HVACTemplate creates in order to add in your ZoneHVAC equipment objects. On 11/15/2011 8:54 AM, amyquartette wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.