[EnergyPlus_Support] Re: SetpointManager:MixedAir and Economizer question



Thanks James. A few more questions, if you'll indulge me...

The referance node:
I assume one must be quite careful as to what setpoint is used on the reference node (usually the last node on the supply side). For example, if my last componant is a heating coil, I can't assign a fixed schedule 32degC with a setpoint manager on the htg coil exit node, if I plan heating and cooling all year round. I need to use, in this case a setpoint manager that can decrease the setpoint on this node during times of cooling. Right?

The other setpoint nodes in the list:
How does the MixedAirSPmanager "know" on which node the fan sits, to deturmine upstream and down stream from it? I don't have it here. Is it an input field? I ask, because not just the fan takes or adds to the air stream. Maybe, it just looks at the setpoint on each node in the list (not the airstream temp), checks if it must be applied (eg. clg sp not applied if in heating mode), and estimates the energy put in or out at these nodes. Using this information, it sets the setpoint at the exit of the mixing box, then the controller tries to control the damper to match. Right?

Please explain "exception 1". My guess is that if the downstream htg coil exit node was included, the manager would see it as a second fan and (if outside had cold air) possibly introduce more than nessecary ODA, which the poor htg coil would have to heat up. This all becomes hellishly complicated considering econimizers and other factors.



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/