Jean, The MixedAir SetpointManager works somewhat differently than the concept of other SetpointManagers. Most SetpointManagers have the purpose of maintaining a specific value (e.g., temperature or humidity) at a node. Here’s how I understand that the :MixedAir version works: Keep in mind that the heat added to the air flow from a fan (normally .5 – 1.5C), affects the cooling or heating process. If the fan is in a draw-through position (downstream of the coil), the cooling coil logic is: · A discharge temperature of, say, 12C is required to satisfy the SetpointManager:Scheduled · The fan (at this particular timestep) adds 1C to the air temperature · So the cooling coil must operate to produce 11C air in order that 12C is achieved at the outlet / discharge AS you mention below, this SetpointManager “knows” whether cooling or heating is in use. This varies a bit for other types of SetpointManagers, such as :SingleZone:Reheat or :Warmest, but is applied in the same manner. The MixedAir SetpointManager has the job
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |