Re: [EnergyPlus_Support] Model a Chiller:Electric or Chiller:Electric:EIR



Well,I've created the EIRFT curve too.Then I've simulated and shown
the Chiller Evap Heat Trans Rate, Chiller Part Load Ratio, and Chiller
Cycling Ratio.
The operations I've done are:
A)Divide "CHILLER:Chiller Evap Heat Trans Rate [W]" by
"CHILLER:Chiller Part Load Ratio" when the "CHILLER:Chiller Cycling
Ratio" is 1.
B)Divide "CHILLER:Chiller Electric Power [W]" by "CHILLER:Chiller COP
[W/W]" when the "CHILLER:Chiller Cycling Ratio" is 1.
C)Look to the condenser "CHILLER:Chiller Cond Water Inlet Temp [C]"
and "CHILLER:Chiller Evap Water Outlet Temp [C]"

With the values from C) I look up on my provider data set and check if
A) is near to the actual operating capacity.
With the values from C) I look up on my provider data set and check if
B) is near to the actual compresor input rate.
Therefore if the values are similar,my model works very similar to the
real chiller.
Is it OK?

Thanks so mucho for your support,
Ignacio Gomis

P.S.:I've added the spreadsheat with the second curve and the values
from a day of my simulation(21th of July)


------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


Content-Type: application/vnd.ms-excel; name="Cooling Capacity.xls"
Content-Disposition: attachment; filename="Cooling Capacity.xls"
X-Attachment-Id: f_gvligwcz0
Attachment not found:
d:\eudora\attach\Cooling Capacity1.xls