Re: [EnergyPlus_Support] Model a Chiller:Electric or Chiller:Electric:EIR
I don't know if i have understood very well the way you told me to
complete the exercise.I've added the new version of the spreadsheet.
Is it possible to model the last curve,"part load ratio curve"?
By the way,checking the simulation values I found a "wrong" value in
my chiller.Energy+ has designed the condenser flow rate is very very
high and therefore the delta temperature in the condenser for the
water is really low.
Water condenser flow rate:4710kg/s
The problem was that I filled the parameter for the design in kg/s and
it is asked in m3/s. Now I think it's solved.
Thanks,
Ignacio Gomis
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
Content-Type: application/vnd.ms-excel; name="Cooling Capacity.xls"
Content-Disposition: attachment; filename="Cooling Capacity.xls"
X-Attachment-Id: f_gvmh1crp1
Attachment not found:
d:\eudora\attach\Cooling Capacity2.xls