[EnergyPlus_Support] Re: Cooling SetPoint depending on inside and outside temperature?



Hello for your feedback,

Yes, the reason is to quantify energy savings using controlled air system to allow air from outside in summer when temperature is below 25C.

So, can I have HVACTamplate:Thermostat and Schdule:Compact to Set Cooling SetPoint to 25C, and Controller:OutdoorAir ??

I am not an expert, I am trying to set up, and I find out that I need to set up AirLoopHVAC also and maybe Set Point Manager.

Cheers,
Jose


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, RRaustad@... wrote:
>
> Sounds like you are talking about an outdoor air economizer which is
> implemented with Controller:OutdoorAir. You don't really want to turn
> off cooling if OA temp is below your limit, since the indoor load could
> be high. So what you want is to bring in OA when it will offset the
> cooling load and reduce energy use.
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/