|
As indicated by the error message, you are running DX cooling in Winter. Jan 14 in Chicago.
Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: eee.javed@xxxxxxxxx Date: Wed, 28 Dec 2011 12:32:54 +0000 Subject: [EnergyPlus_Support] Warning for Coil:Cooling:DX:SingleSpeed
Hi All,
I am trying to run DX cooling coil and getting following repetitive error , what could be the possible solution for the same. ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE5-1 PTAC COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = -4.83 C. ** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 01/14 08:38 - 08:45 ** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil ** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 10.835 C. ** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs. ** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs. ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE3-1 PTAC COOLING COIL" - Air-cooled condenser inlet dry-bulb temperature below 0 C. Outdoor dry-bulb temperature = -4.40 ** ~~~ ** ... Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 01/14 10:00 - 10:15 ** ~~~ ** ... Operation at low ambient temperatures may require special performance curves. ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE3-1 PTAC COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = 8.52E-002 C. ** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 01/14 10:00 - 10:15 ** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil ** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 15.011 C. ** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs. ** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs. ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE1-1 PTAC COOLING COIL" - Air-cooled condenser inlet dry-bulb temperature below 0 C. Outdoor dry-bulb temperature = -4.40 ** ~~~ ** ... Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 01/14 10:45 - 11:00 ** ~~~ ** ... Operation at low ambient temperatures may require special performance curves. ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE1-1 PTAC COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = 1.79 C. ** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 01/14 15:00 - 15:15 ** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil ** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 15.972 C. ** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs. ** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs. ************* Simulation Error Summary ************* ************* ************* ===== Recurring Error Summary ===== ************* The following recurring error messages occurred. ************* ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE5-1 PTAC COOLING COIL" - Low condenser dry-bulb temperature error continues... ************* ** ~~~ ** This error occurred 45 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=-2.8 [C] Min=-7.2 [C] ************* ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE5-1 PTAC COOLING COIL" - Full load outlet temperature indicates a possibility of frost/freeze error continues. Outlet air temperature statistics follow: ************* ** ~~~ ** This error occurred 45 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=-2.888928 Min=-4.833602 ************* ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "SPACE3-1 PTAC COOLING COIL" - Low condenser dry-bulb temperature error continues... ************* ** ~~~ ** This error occurred 26 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=-2.8 [C] Min=-4.75 [C] Any help is appreciated. Thanks! __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |