There are three parts in defining a blind operation. (not including the schedules)
 
1) in the material and construction
2) in the window object itself to define the control to use.
3) the blind control. (WindowProperty:ShadingControl:)

It is possible that the other two parts were not defined.
 
!- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:BLIND ===========

WindowMaterial:Blind,
Window Blind, !- Name
Vertical, !- Slat Orientation
0.1, !- Slat Width {m}
0.1, !- Slat Separation {m}
0.001, !- Slat Thickness {m}
180, !- Slat Angle {deg}
1, !- Slat Conductivity {W/m-K}
0.1, !- Slat Beam Solar Transmittance
0.3, !- Front Side Slat Beam Solar Reflectance
0.3, !- Back Side Slat Beam Solar Reflectance
0.1, !- Slat Diffuse Solar Transmittance
0.3, !- Front Side Slat Diffuse Solar Reflectance
0.3, !- Back Side Slat Diffuse Solar Reflectance
0.05, !- Slat Beam Visible Transmittance
, !- Front Side Slat Beam Visible Reflectance
, !- Back Side Slat Beam Visible Reflectance
0.05, !- Slat Diffuse Visible Transmittance
, !- Front Side Slat Diffuse Visible Reflectance
, !- Back Side Slat Diffuse Visible Reflectance
, !- Slat Infrared Hemispherical Transmittance
0.2, !- Front Side Slat Infrared Hemispherical Emissivity
0.2, !- Back Side Slat Infrared Hemispherical Emissivity
0.1, !- Blind to Glass Distance {m}
0.05, !- Blind Top Opening Multiplier
0.05, !- Blind Bottom Opening Multiplier
0.05, !- Blind Left Side Opening Multiplier
0.05, !- Blind Right Side Opening Multiplier
, !- Minimum Slat Angle {deg}
180; !- Maximum Slat Angle {deg}
!-  =========================
 
Construction,
Window+Glass+Blind, !- Name
GREY 3MM, !- Outside Layer
Window Blind; !- Layer 2
!- ============================
 
WindowProperty:ShadingControl,
WindowBControl, !- Name
InteriorBlind, !- Shading Type
Window+Glass+Blind, !- Construction with Shading Name
OnIfScheduleAllows, !- Shading Control Type
ON, !- Schedule Name
, !- Setpoint {W/m2, W or deg C}
Yes, !- Shading Control Is Scheduled
No, !- Glare Control Is Active
, !- Shading Device Material Name
FixedSlatAngle, !- Type of Slat Angle Control for Blinds
; !- Slat Angle Schedule Name

!- ====================

Window,

Unit1:S(Rm)Window, !- Name

WINDOW(+Glass), !- Construction Name

Unit1:SWall , !- Building Surface Name

    WindowBControl, !- Shading Control Name

, !- Frame and Divider Name

1, !- Multiplier

0.42, !- Starting X Coordinate {m}

0.9, !- Starting Z Coordinate {m}

1.2, !- Length {m}

1.2; !- Height {m}

!- =======================

 

The window object you use may be different.  But there is a field for the control.  If this is left out as blank, the blind, if defined in construction,  would be left open.

 

The same control may be used for all the windows.

======================
There are more than one way to define the construction and control.  These are described in detail in the I/O Manual.  The error message will tell you wither the construction and window object were declared correctly.Hope this would hel;.
 
 Dr. Li  

 

To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: alexiskirk2000@xxxxxxxx
Date: Sun, 15 Jan 2012 17:47:29 +0000
Subject: [EnergyPlus_Support] Blinds not referenced by windows

 
Dear All,
I ve been trying to introduce the use of blinds in order to reduce the cooling loads of a ground floor house and i keep getting the warning:
GetSurfaceData: WindowProperty:ShadingControl: "BLIND" is not referenced by any window. The window material:blind was taken by the Energy Plus Library and then i created an object in WindowProperty:ShadingControl. Taking into consideration that i have done everything according to the input/output reference where it is mentioned that Window property:shading control is referenced by windows and glass doors, I can not think of anything wrong. I could use your valuable advices. Thank you very much.




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___