[EnergyPlus_Support] Re: Blinds not referenced by windows



Thank you very much, i forgot to reference the shading control name in the fenestration surface detailed object.Works now!

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote:
>
> 
> 
> 
> 
> There are three parts in defining a blind operation. (not including the schedules)
>  
> 1) in the material and construction 
> 2) in the window object itself to define the control to use.
> 3) the blind control. (WindowProperty:ShadingControl:)
> 
> It is possible that the other two parts were not defined.
>  
> !-   ===========  ALL OBJECTS IN CLASS: WINDOWMATERIAL:BLIND ===========
> 
> 
> 
> WindowMaterial:Blind,
>     Window Blind,            !- Name
>     Vertical,                !- Slat Orientation
>     0.1,                     !- Slat Width {m}
>     0.1,                     !- Slat Separation {m}
>     0.001,                   !- Slat Thickness {m}
>     180,                     !- Slat Angle {deg}
>     1,                       !- Slat Conductivity {W/m-K}
>     0.1,                     !- Slat Beam Solar Transmittance
>     0.3,                     !- Front Side Slat Beam Solar Reflectance
>     0.3,                     !- Back Side Slat Beam Solar Reflectance
>     0.1,                     !- Slat Diffuse Solar Transmittance
>     0.3,                     !- Front Side Slat Diffuse Solar Reflectance
>     0.3,                     !- Back Side Slat Diffuse Solar Reflectance
>     0.05,                    !- Slat Beam Visible Transmittance
>     ,                        !- Front Side Slat Beam Visible Reflectance
>     ,                        !- Back Side Slat Beam Visible Reflectance
>     0.05,                    !- Slat Diffuse Visible Transmittance
>     ,                        !- Front Side Slat Diffuse Visible Reflectance
>     ,                        !- Back Side Slat Diffuse Visible Reflectance
>     ,                        !- Slat Infrared Hemispherical Transmittance
>     0.2,                     !- Front Side Slat Infrared Hemispherical Emissivity
>     0.2,                     !- Back Side Slat Infrared Hemispherical Emissivity
>     0.1,                     !- Blind to Glass Distance {m}
>     0.05,                    !- Blind Top Opening Multiplier
>     0.05,                    !- Blind Bottom Opening Multiplier
>     0.05,                    !- Blind Left Side Opening Multiplier
>     0.05,                    !- Blind Right Side Opening Multiplier
>     ,                        !- Minimum Slat Angle {deg}
>     180;                     !- Maximum Slat Angle {deg}
> !-  =========================
>  
> Construction,
>     Window+Glass+Blind,      !- Name
>     GREY 3MM,                !- Outside Layer
>     Window Blind;            !- Layer 2
> 
> !- ============================
>  
> WindowProperty:ShadingControl,
>     WindowBControl,          !- Name
>     InteriorBlind,           !- Shading Type
>     Window+Glass+Blind,      !- Construction with Shading Name
>     OnIfScheduleAllows,      !- Shading Control Type
>     ON,                      !- Schedule Name
>     ,                        !- Setpoint {W/m2, W or deg C}
> 
> Yes,                     !- Shading Control Is Scheduled
>     No,                      !- Glare Control Is Active
>     ,                        !- Shading Device Material Name
>     FixedSlatAngle,          !- Type of Slat Angle Control for Blinds
>     ;                        !- Slat Angle Schedule Name
> 
> 
> 
> !- ====================Window,    Unit1:S(Rm)Window,       !- Name    WINDOW(+Glass),          !- Construction Name    Unit1:SWall ,            !- Building Surface Name    WindowBControl,                        !- Shading Control Name    ,                        !- Frame and Divider Name    1,                       !- Multiplier    0.42,                    !- Starting X Coordinate {m}    0.9,                     !- Starting Z Coordinate {m}    1.2,                     !- Length {m}    1.2;                     !- Height {m}!- ======================= The window object you use may be different.  But there is a field for the control.  If this is left out as blank, the blind, if defined in construction,  would be left open. The same control may be used for all the windows.
> ======================There are more than one way to define the construction and control.  These are described in detail in the I/O Manual.  The error message will tell you wither the construction and window object were declared correctly.Hope this would hel;.
>  
>  Dr. Li   
>  
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: alexiskirk2000@...
> Date: Sun, 15 Jan 2012 17:47:29 +0000
> Subject: [EnergyPlus_Support] Blinds not referenced by windows
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
>  
> 
> 
> 
>   
> 
> 
>     
>       
>       
>       Dear All,
> 
> I ve been trying to introduce the use of blinds in order to reduce the cooling loads of a ground floor house and i keep getting the warning:
> 
> GetSurfaceData: WindowProperty:ShadingControl: "BLIND" is not referenced by any window. The window material:blind was taken by the Energy Plus Library and then i created an object in WindowProperty:ShadingControl. Taking into consideration that i have done everything according to the input/output reference where it is mentioned that Window property:shading control is referenced by windows and glass doors, I can not think of anything wrong. I could use your valuable advices. Thank you very much.
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/