Laurent,

 

I did a quick run of your model and it looks like your spaces are reaching temperatures above your cooling setpoint of 24.4C during the winter months, causing the cooling coils to enable at very low outside air temps.  This is probably due to either your internal loads being too high and/or a really tight envelope and/or practically no outside air going into the spaces (0.5 CFM for each RTU).  Hope this helps!

 

Thanks, 

 

Matthew Larson, CEM, LEED AP BD+C
Project Engineer

Energy Solutions Group

Eaton’s Electrical Services & Systems
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239

MatthewRLarson@xxxxxxxxx
www.eaton.com/energysolutions 

Description: image001

 

From: EnergyPlus_Sup

__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00210.png