For the other warnings: The roof is curved, and look normal on the DXF. However, the object itself seems to be in error. One of the surface which has a warning is show below. ===================. BuildingSurface:Detailed, 41A989, !- Name Roof, !- Surface Type INSULATION ABOVE DECK, !- Construction Name Tenant 5, !- Zone Name Outdoors, !- Outside Boundary Condition , !- Outside Boundary Condition Object SunExposed, !- Sun Exposure WindExposed, !- Wind Exposure , !- View Factor to Ground 4, !- Number of Vertices -26.402536646104, 28.390207384233, 5.689600000000, !- X,Y,Z 1 {m} -26.402536646104, 28.390207384233, 4.911994336072, !- X,Y,Z 2 {m} -27.592535976135, 27.908390562012, 5.202118134911, !- X,Y,Z 3 {m} -27.592535976135, 27.908390562012, 5.689600000000; !- X,Y,Z 4 {m} ====================== two (x,y) points at Z1=Z4, and the other two Z's are on the same vertical surface with 90 degree view angle. Normally, there should be two parallel lines at different height. If the lines are not parallel, the surface has to be broken up into two triangles. I do not use DesignBilder or OpenStudio, but is easy to fix using the EPlus MACRO. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: brent.griffith@xxxxxxxx Date: Wed, 18 Jan 2012 14:11:56 -0700 Subject: RE: [EnergyPlus_Support] Warning for Coil:Cooling:DX:SingleSpeed Those warnings are difficult to remove and can usually be ignored. It is rather common for interior zones with high internal gains and no infiltration to require cooling in the middle of winter. Real equipment might shut off or run heaters to protect the unit, but the simulation does not (yet) model that well so it issues the warning.
From a design perspective, getting those errors should suggest considering air-side economizing and that the real equipment will need to have cold-weather protection.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Laurent Kanago
I saw this post earlier but I still don't understand why the DX cooling is running in the wintertime. I followed the example for Packaged Unitary systems and the thermostats are set. Is the problem the Cooling Coil Schedules? I would assume the the coiling coils should be allowed to stay "always on."
** Warning ** Coil:Cooling:DX:SingleSpeed "RTU-4 COOLING COIL" - Air-cooled condenser inlet dry-bulb temperature below 0 C. Outdoor dry-bulb temperature = -2.93 ** ~~~ ** ... Occurrence info = CHICAGO WEATHER, 01/03 12:30 - 12:45 ** ~~~ ** ... Operation at low ambient temperatures may require special performance curves. ** Warning ** Coil:Cooling:DX:SingleSpeed "RTU-5 COOLING COIL" - Air-cooled condenser inlet dry-bulb temperature below 0 C. Outdoor dry-bulb temperature = -2.80 ** ~~~ ** ... Occurrence info = CHICAGO WEATHER, 01/03 12:45 - 13:00 ** ~~~ ** ... Operation at low ambient temperatures may require special performance curves. ** Warning ** Coil:Cooling:DX:SingleSpeed "RTU-1 COOLING COIL" - Air-cooled condenser inlet dry-bulb temperature below 0 C. Outdoor dry-bulb temperature = -2.80 ** ~~~ ** ... Occurrence info = CHICAGO WEATHER, 01/03 13:00 - 13:15 ** ~~~ ** ... Operation at low ambient temperatures may require special performance curves. ** Warning ** Coil:Cooling:DX:SingleSpeed "RTU-3 COOLING COIL" - Air-cooled condenser inlet dry-bulb temperature below 0 C. Outdoor dry-bulb temperature = -2.80 ** ~~~ ** ... Occurrence info = CHICAGO WEATHER, 01/03 13:00 - 13:15 ** ~~~ ** ... Operation at low ambient temperatures may require special performance curves.
Any reply would help.
Thanks,
Laurent Kanago Technology Director
Office: (312) 235-2225 Fax: (773) 989.8679 Cell: (312) 730-2419 5030 N. Marine Dr #807 Chicago, IL 60640 http://www.ecohillsolutions.com/
?Please consider the environment before printing this e-mail. Thank you.?
From: YuanLu Li <yli006@xxxxxxxxxxx>
As indicated by the error message, you are running DX cooling in Winter. Jan 14 in Chicago. To: EnergyPlus_Support@xxxxxxxxxxxxxxx Hi All, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional