The model should be able to handle the slave zones okay. It looks at the relative flow rates (from sizes of air terminals) between the controlling zone and the slave zones on the air handler and then scales up the loads as if all the slave zones had the same load as the controlling zone. A work around to get better control is to thermally couple the slave zones and the control zone using balanced pairs of ZoneMixing objects with relatively high flow rates. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of luke_dorna I am currently using the the AirLoopHVAC:UnitaryHeatPump:WaterToAir object to model distributed heat pumps throughout a building. Unfortunately, the object only allows for a single controlling thermostat, but the design calls for heat pumps that serve multiple rooms. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.