Hi Luke, In the "Catalog Data" tab, the data points must have varying inlet conditions which covers entire range of heat pump operation. There should be at least 6 data points and flow rates/temperatures columns must not be constant. If the manufacturer has provided you correction factors to extend the performance data, it would help to generate more accurate coefficients. In general equation fit model is preferred over parameter estimation model and one of the reason is that curve fit coefficients are easier to calculate. Also, the curve fit model allows you to calculate coefficients for 410A. "Rated..." values in the CoeffCalculator tab also affect the curve fit coefficients. Hope this helps. Chandan On 1/26/2012 3:16 PM, luke_dorna wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.