The cut sheet I have has constant load side air temp and flow with varying source side water flow and temp. When you say these cannot be constant, do both load and source side have to vary, or just the source?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Chandan Sharma <csharma@...> wrote:
>
> Hi Luke,
> 
> In the "Catalog Data" tab, the data points must have varying inlet 
> conditions which covers entire range of heat pump operation. There 
> should be at least 6 data points and flow rates/temperatures columns 
> must _not_ be constant.
> If the manufacturer has provided you correction factors to extend the 
> performance data, it would help to generate more accurate coefficients. 
> In general equation fit model is preferred over parameter estimation 
> model and one of the reason is that curve fit coefficients are easier to 
> calculate. Also, the curve fit model allows you to calculate 
> coefficients for 410A.
> 
> "Rated..." values in the CoeffCalculator tab also affect the curve fit 
> coefficients.
> 
> Hope this helps.
> Chandan
> 
> 
> 
> On 1/26/2012 3:16 PM, luke_dorna wrote:
> >
> > I am currently trying to generate the equation fit coefficients for a 
> > water to air heat pump cooling coil. Unfortunately, the 
> > waterair_pe_cooling.xls file seems to be giving me an incorrect result 
> > with average % of over 100.
> >
> > Has anyone run into a situation like this? It looks like can get a 
> > better result from the parameter estimation method, however it does 
> > not support 410a, which is the refrigerant from the design.
> >
> > Thanks,
> >
> > Luke
> >
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/