The warning is telling you that in the schedule VACACIONES does not have all the day types specified. There are twelve of them, and they may be grouped as weekends, weekdays, allDays, and allOtherDays. AllDays (no space between the words) covers all the types. I.e. same set of value for all the days.
The error said that the last day field was "For:Holiday". Therefore, Weekdays, DesignDays, CumstomDays as listed were not specified. 0.0 will be used for these day types. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jomeluque@xxxxxxxx Date: Thu, 26 Jan 2012 20:00:57 +0000 Subject: [EnergyPlus_Support] 21 Warning ,schedule
Someone could help me with this Warning, because I have 21 of the same type and gives me something I should be doing it wrong
(Spanish)Alguien me podria ayuda con este Warning, ya que tengo 21 del mismo tipo y me da que algo debo estar haciendo mal ** Warning ** ProcessScheduleInput: Schedule:Compact="VACACIONES" has missing day types in Through=12/31 ** ~~~ ** Last "For" field=FOR: HOLIDAY ** ~~~ ** Missing day types="Sunday","Monday","Tuesday","Wednesday","Thursday","Friday","Saturday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2" ** ~~~ ** Missing day types will have 0.0 as Schedule Values __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |