[EnergyPlus_Support] Re: Modeling DHW Use
You're basically right on.
Technically, what you would do would be to determine total flow rate of the fixtures in the room. Then, enter that into the peak flow rate of line of the wateruse:equipment element.
Then create a schedule for the line item "flow rate fraction schedule name"
See below.
WaterUse:Equipment,
DHW Cafeteria, !- Name
DHW Cafeteria, !- End-Use Subcategory
0.0007, !- Peak Flow Rate {m3/s}
Cafeteria DHW, !- Flow Rate Fraction Schedule Name
DHW Supply Temperature, !- Target Temperature Schedule Name
DHW Supply Temperature, !- Hot Water Supply Temperature Schedule Name
DHW Mains Temperature, !- Cold Water Supply Temperature Schedule Name
F1:Cafe; !- Zone Name
Schedule:Compact,
Cafeteria DHW, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 10:00,0, !- Field 3
Until: 11:00,0.2, !- Field 5
Until: 14:00,0.88, !- Field 7
Until: 15:00,0, !- Field 9
Until: 18:00,0.2, !- Field 11
Until: 24:00,0; !- Field 13
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ke Xu" <xukevin24@...> wrote:
>
> Dear all,
> I added a DHW loop in E+ model, so I have 2 water heaters and several outlets as "wateruse:equipment". I wasn't sure what to enter for the "Peak flow rate" for each outlet, is it related with the "Use side Design Flow Rate" as an input of class "waterheater:mixed"?
>
> I would expect that modeling the demand side of DHW loop is kinda of similar with modeling lighting system, you would input a demand density number, such as Gal/ft2-day, then by multiplying the zone area, we get the peak flow rate, etc, and by multiplying a schedule, we get amount of DHW demand for each hour, right?
>
> Thanks in advance.
>
> ---Ke
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/