[EnergyPlus_Support] Re: Zone mean temperature...
Hi Dr Li,
I have uploaded a file titled synergy HVAC. Could you please take a look and explain the sizing problem? It would really solve my trouble in getting the correct zone mean temperature.
Best regards,
Sky Lo
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "skyduo85" <skyduo@...> wrote:
>
> Hi Dr Li,
>
> I am not sure where i can find the sizing multiplier but the figures in my HVAC system are all autosized. Pls advice.
>
> Best regards,
> Sky Lo
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@> wrote:
> >
> >
> > A simple answer for ZAT not at the setpoint is that the system is not designed or sized properly. The quick solution for "zone set point not met" is to increasing the sizing multiplier for the VAV fan, so that the VAV damper setting at Unity has a larger air flow to the zone, to cool the return air at the AHU. Adjusting the chiller size usually has no effect, as the problem is not a limitation of the cooling supply. It is a problem that the VAV fan cannot increase its flow rate to extract more cooling capacity from the cooling coil to meet the zone demand, when the zone VAV damper is opened to its maximum..===================="zone uncomfortable" is not the same as "zone setpoint not met". However, they can be related when the ZMT is set to the limit of the comfort range.
> >
> > Dr. Li
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > From: skyduo@
> > Date: Fri, 10 Feb 2012 09:47:57 +0000
> > Subject: [EnergyPlus_Support] Zone maean temperature...
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > Hi,
> >
> >
> >
> > I am running a full detailed central vav HVAC, everything is running ok but when i want it to generate the 'no. of not comfortable hr' to check the chiller size, it indicate all zone uncomfortable. I tried to adjust the thermostat but the zone mean temperature didnt not change. May i ask how and what i should do to get the desired result?
> >
> >
> >
> > Best regards,
> >
> > Sky Lo
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/