Dear Luke, How about: · Acknowledging that the actual system will do exactly as your model suggests (operate at 100% until it meets the occupied period set point) If the actual system has provisions for gradual startup, it might be accomplished by: · Limiting which systems can operate (a demand limiting scheme) · Ramping the zone setpoints gradually from their unoccupied values to the occupied values · (If you have a VAV system) ramping the fan maximum speed gradually so it cannot call for 100% all at once. I’m just brainstorming; I have not seen any of these except the demand limiting and have not modeled any of them
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.