Calculated U values are shown in the output file (.eio) when you add the report for Constructions:

Output:Constructions,Constructions,Materials;

The object is described in the Input Output reference and the output in the Output Details documents.  These are shown without film coefficients because film coefficients vary during the simulation.

To change the U value, you would need to change the inputs.

Output:At 02:14 AM 2/23/2012, Eng.Amin M. wrote:


Thanks for your helpful answers,
I still have a question regarding this class:
After I define the materials and input them, How can I know the total U value of the construction? because our local codes oblige us now to exceed certain value for each construction. Is there anyway -after knowing U value- to modify it?
 
Regards,
 


To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: linda@xxxxxxxxxxxxxx
Date: Wed, 22 Feb 2012 10:35:53 -0700
Subject: Re: [EnergyPlus_Support] Re: Material & Material:NoMass

 
That is a problem that is being worked on for the next release.

At 10:18 AM 2/22/2012, CleanTech Analytics wrote:

Also I have noticed that the finite difference algorithm for simulating Phase Change Materials does not converge when any materials no mass are used.
On Wed, Feb 22, 2012 at 8:07 AM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 
That is correct, if you have some layers with nomass, the whole construction will still be okay (providing thermal mass properties to the building) if they are using the "regular" properties.
At 09:02 AM 2/22/2012, Jean marais wrote:
just that layer has no mass, not the whole contruction...? I.e. I assume that a no mass layer does not nullyfy the internalmass of the entire contruction, right?




--
Jeremiah D. Crossett
CleanTech Analytics
503-688-8951
www.cleantechanalytics.com
[]  
This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics








__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___