You probably need to choose a “FullInterior*” type of Solar Distribution in the Building object. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of aanaranj Hi
** Severe ** ComputeIntSolarAbsorpFactors: Solar distribution model is set to place solar gains on the zone floor, What could I do for making my tilted floor to absorb solar gains? As suggested for the error report, I check the solar absortance of the inside layer of that floor. That solar absortance is set to: 0.85
There´s also a severe error on shadowing calculations: ** Severe ** DetermineShadowingCombinations: There are 1 surfaces which are casting surfaces and are non-convex. Regards __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.