[EnergyPlus_Support] Re: Low Temperature Radiant Cooling Won't Meet Loads



Monitor the surface temp of your radiant system. monitor the mass flow rates. I would hard size the pipes and mass flow rates realistically (the autosizing at the, for radiant system, conditions may be wrong). Hard size. The setpoint in the lowtemprad object should be lower than that of the zone SP by about 2 degC.

For chilled ceiling you'll get realistically a max of 75 W/m2, and for a floor 20-40 W/m2 at Roomtemp 26degC and surface temps 16 degC. These systems are limited by fundimentals of heat transfer via radiation and convection. Even blowing air across to increase the convection transfer has minimal effect. 

Do some hand calcs. Let us know how you get on.



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/