Re: [EnergyPlus_Support] Convergence issue-- does this matter?




We've done some work on these algorithms -- I suggest you send it to the helpdesk and we can run it on the dev engine.

(by the way, it looks like it might converge in a few more iterations).

On 20.03.2012 19:36, CleanTech Analytics wrote:
Dear List, 
I have been working on this file for many a days, attempting to have a
warning free run. 
The simulation is for a Phase Change Material, and is producing good
results so far as energy savings, heat flux reduction, HVAC size
reduction, and Peak load reduction.  The file is to be used in a
climate study of various melt temperatures, so determine best product
for each ASHRAE climate.
There are no errors without the PCM, and I have all three convergence
settings, and relaxation at max values (the file did not work with
lower)

I realize I could ignore this, but would like to figure out the issue
and fix it if at all possible... Thanks

Program Version,EnergyPlus-64 7.0.0.036, 3/20/2012 4:37 PM,IDD_Version
7.0.0.036
   ************* Beginning Zone Sizing Calculations
    ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.344E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=COOL, at Simulation
time=08/21 05:16 - 05:18
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.288E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=COOL, at Simulation
time=08/21 07:28 - 07:30
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.199E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=COOL, at Simulation
time=08/21 09:56 - 09:58
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.106E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=COOL, at Simulation
time=08/21 12:08 - 12:10
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.005E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=COOL, at Simulation
time=08/21 15:16 - 15:18
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.170E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=COOL, at Simulation
time=08/21 18:44 - 18:46
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.018E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=HEAT, at Simulation
time=02/21 09:46 - 09:48
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.401E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=HEAT, at Simulation
time=02/21 15:46 - 15:48
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.421E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  During Sizing, Environment=HEAT, at Simulation
time=02/21 17:32 - 17:34
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity
   ************* All Return Air Paths passed integrity testing
   ************* No node connection errors were found.
   ************* Beginning Simulation
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.347E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  Environment=COOL, at Simulation time=08/21
05:16 - 05:18
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.288E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  Environment=COOL, at Simulation time=08/21
07:28 - 07:30
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.199E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  Environment=COOL, at Simulation time=08/21
09:56 - 09:58
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.105E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  Environment=COOL, at Simulation time=08/21
12:08 - 12:10
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.005E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  Environment=COOL, at Simulation time=08/21
15:16 - 15:18
   ** Warning ** Inside surface heat balance did not converge with
Max Temp Difference [C] =1.170E-002 vs Max Allowed Temp Diff [C]
=1.000000E-002
   **   ~~~   **  Environment=COOL, at Simulation time=08/21
18:44 - 18:46
   ************* Simulation Error Summary *************
   *************
   ************* ===== Recurring Error Summary =====
   ************* The following recurring error messages occurred.
   *************
   *************  ** Warning ** Inside surface heat balance
convergence problem continues
   *************  **   ~~~   **   This error occurred 459 total
times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.
   *************  **   ~~~   **   Max=5.370517E-002 [C]
 Min=9.900995E-003 [C]
   *************
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0
Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 9
Warning; 0 Severe Errors.
   ************* EnergyPlus Completed Successfully-- 474 Warning; 0
Severe Errors; Elapsed Time=00hr 26min 21.93sec

_Jeremiah D. Crossett_
_CleanTech Analytics_
_503-688-8951_

_www.cleantechanalytics.com_ [1]

 This document may contain valuable information proprietary to
CleanTech Analytics which is private and confidential. It may not be
shared, copied, stored or transmitted in any form without the prior
written consent of CleanTech Analytics

__._,_.___

  Primary EnergyPlus support is found at:
 http://energyplus.helpserve.com [2] or send a message to
energyplus-support@xxxxxxxx

 The primary EnergyPlus web site is found at:
 http://www.energyplus.gov [3]

 The group web site is:
 http://groups.yahoo.com/group/EnergyPlus_Support/ [4]

 Attachments are currently allowed but be mindful that not everyone
has a high speed connection. Limit attachments to small files.

 EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
the Documentation link and press the "search" button.

 Your email settings: Individual Email|Traditional
 Change settings via the Web [5] (Yahoo! ID required)
 Change settings via email: Switch delivery to Daily Digest [6] |
Switch to Fully Featured
  Visit Your Group  [7] |  Yahoo! Groups Terms of Use  [8] |
Unsubscribe  [9]

__,_._,___

Links:
------
[1] http://www.cleantechanalytics.com
[2] http://energyplus.helpserve.com
[3] http://www.energyplus.gov
[4] http://groups.yahoo.com/group/EnergyPlus_Support/
[5]

http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmc3NpNGRyBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMzIyOTM3ODM-
[6]

mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=EmailDelivery:Digest
[7]

http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkaGxwc3BiBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzMyMjkzNzgz
[8] http://docs.yahoo.com/info/terms/
[9] mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe