Thanks for taking the time to clarify. This makes sense.
Liam
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Cooling Coil Sensible Cooling Rate reports the coil cooling rate so you should see 0 when the coil is off
>
> Fan Coil Sensible Cooling Rate reports the overall cooling rate of the fan coil unit, including coil operation, outdoor air impact, and fan heat. It's basically Q = Mdot * deltaH from fan coil inlet to outlet. Since the inlet is the zone exhaust node, then it's the impact of the energy transfer from the supply air leaving the fan coil with respect to the zone conditions. As long as the fan is on, this report will be non-zero (and never 0 or very rarely coincidentally 0)
>
> Zone/Sys Sensible Cooling Rate is the impact of all the zone inlet nodes
> added up (plus a few extra terms for special equipment) so this report
> should match the Fan Coil Sensible Cooling Rate report variable (there
> may be a time lag of 1 time step, I can't recall).
>
> Use detailed reporting frequency when you are troubleshooting equipment
> operation in detail (no averaging involved in reported values).
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/