You need to take your search for answers back to any basic thermodynamics text you may have ever studied. In a steady state heat transfer calculation, one
can ignore the heat storage capacity of any of the materials in the heat flow path. However a transient calculation needs to consider that the materials themselves store and emit heat as their temperature changes. Heavy weight materials more so than lightweight
materials. By extension in Energy+, you can’t change the temperature of a room without also storing or extracting energy from all the objects in the room including floors, walls, and ceilings. Energy+ will do this for all your surfaces if you fully define them. There are also provisions for considering other contents of the room that are nor defined
in the floors, walls, and ceilings (internal mass objects). The how is in the engineering reference documents, the why is basic physics….
Ned Lyon, P.E. (MA) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Amir Thanks for reply. I did take a look at and searched through most of the Energy Plus documents available on the website. Although thermal mass and its applications in Energy Plus are repeatedly mentioned in these documents, I
still could not find the basic fundamentals behind the consideration of thermal mass itself. The very basic methods that were used to introduce the concept of thermal mass in the Energy Plus program in the first place. Any help?
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.