Re: [EnergyPlus_Support] Ventilation Requirements per ASHRAE 90.1 Appendix G with a DOAS system





You could hardwire the same OA cfm for each zone to what it is in the design case.

On Tue, Apr 3, 2012 at 11:55 AM, curtisjclark <cjcfromslc@xxxxxxxxx> wrote:
 

We are using a DOAS system which delivers 100% outdoor air to the space. In the Baseline model (appendix G), it is a VAV system which delivers mixed outdoor air with return air.

To meet the requirements of ASHRAE 62.1 in the Baseline model, I used the Ventilation Rate Procedure calculation method to determine the minimum outdoor air by using the Controller:MechanicalVentilation object with the same ventilation rates as in the DOAS system.

The report for "Controller:OutdoorAir" shows the two system have same Minimum Outdoor Air Flow Rate. However, the report "Minimum Outdoor Air During Occupied Hours" shows a 84% reduction in outdoor air.

Have I meet the requirements of Appendix G3.1.2.6 for ventilation?




--
Vinay Dev



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___