[EnergyPlus_Support] Re: Ventilation Requirements per ASHRAE 90.1 Appendix G with a DOAS system



Each zone is hardwired using DesignSpecification:OutdoorAir object using "Flow/Area" values.

Curtis

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Vinay Devanathan <vinay.devanathan@...> wrote:
>
> You could hardwire the same OA cfm for each zone to what it is in the
> design case.
> 
> On Tue, Apr 3, 2012 at 11:55 AM, curtisjclark <cjcfromslc@...> wrote:
> 
> > **
> >
> >
> > We are using a DOAS system which delivers 100% outdoor air to the space.
> > In the Baseline model (appendix G), it is a VAV system which delivers mixed
> > outdoor air with return air.
> >
> > To meet the requirements of ASHRAE 62.1 in the Baseline model, I used the
> > Ventilation Rate Procedure calculation method to determine the minimum
> > outdoor air by using the Controller:MechanicalVentilation object with the
> > same ventilation rates as in the DOAS system.
> >
> > The report for "Controller:OutdoorAir" shows the two system have same
> > Minimum Outdoor Air Flow Rate. However, the report "Minimum Outdoor Air
> > During Occupied Hours" shows a 84% reduction in outdoor air.
> >
> > Have I meet the requirements of Appendix G3.1.2.6 for ventilation?
> >
> >  
> >
> 
> 
> 
> -- 
> Vinay Dev
>



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/