Thank you very much Rechard !

But the thing is, where the air exits the building matters in my model, becuase it's a multizone air flow model. That is, the OA exits through the internal window to the next zone which is an atria as a chimney effect.

Is there a way that I can make the air flow to start from OA mixer--> zone 1 --> zone 2(atria), not allowing return air or exhaust fan operation? 

Thank you in advance!

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Correct. But unless you use exhaust fan to expel the air, the return 
> flow rate will not be 0 so you will have to make sure the return air 
> gets exhausted at the OA mixer. It really doesn't matter where the air 
> exits the building, so either ensure 100$ OA or exhaust the same amount 
> of supply air from the zone.
> 
> On 4/12/2012 4:43 AM, denergyplus wrote:
> > Hi all!
> >
> > I am currently working on a DOAS that has no return or relief air because all the OA supplied is being exhausted through the window at the zone.
> >
> > But, 'AirLoopHVAC' fields require Supply Side Inlet Node Name and Demand Side Outlet Node Name, which aren't part of my system.
> >
> > Should I just input those fields and control the their flow to be zero?
> >
> > Thank you in advance.
> >
> >
> >
> > ------------------------------------
> >
> > Primary EnergyPlus support is found at:
> > http://energyplus.helpserve.com or send a message to energyplus-support@...
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/