If you want to change the expIDF file, you should do it for one zone and watch the result.
It is waste of time to change all 22 zones and do not know why. Run your template version again and note all the flowrates. In your country cooling is priority 1. Heating is optional. It will be easier to change the values in the template, rather then in the expIDF. Run cooling only and see whether you need any heating.
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: eee.javed@xxxxxxxxx Date: Sat, 14 Apr 2012 06:31:48 -0700 Subject: [EnergyPlus_Support] Warning in VRV modeling Hi, I am modeling VRV system for proposed case and getting following error on almost all Outdoor Unit. I tried with Increase and decrease in Temp but it didn't work. Kindly Guide me on this. Please find attached file for the same.
** Warning ** AirConditioner:VariableRefrigerantFlow "VRF HEAT PUMP (18+18+10HP)".
** ~~~ ** ...InitVRF: VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode Limits have been exceeded and VRF system is disabled. ** ~~~ ** ... Outdoor Dry-Bulb Temperature = 18.395
** ~~~ ** ... Heating Minimum Outdoor Dry-Bulb Temperature = -20.000 ** ~~~ ** ... Heating Maximum Outdoor Dry-Bulb Temperature = 17.000 ** ~~~ ** ... Check VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode limits.
** ~~~ ** During Warmup, Environment=PUNE ANN CLG 1% CONDNS WB=>MDB, at Simulation time=05/21 00:00 - 00:15 Thanks! Javed Iqbal, LEED AP, CEA
Energy Analyst
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.