[EnergyPlus_Support] Does the infiltration flow rate in EnergyPlus corrected for wind speed ?



When I last attempted to convert DOE-2.1E input files to EnergyPlus about five years ago, 
a coworker and I found a consistent 30% or so increase in the infiltration rate calculated 
by EnergyPlus as compared to DOE-2, which we ultimately tracked down to the fact that the 
infiltration model in DOE-2 was using the adjusted wind speed for terrain factors, while 
the infiltration model in EnergyPlus was using the unadjusted wind speed from the weather 
file. Therefore,
to obtain the same amount of infiltration in both models, we adjusted the input 
infiltration flow rate in EnergyPlus by a correction factor for the terrain, somewhere 
around 0.648 for the assumed terrain condition.  Is that still necessary today, or is the 
infiltration model in EnergyPlus now also using the corrected wind speed rather than the 
raw wind speed from the weather file (most often measured at an airport) ?

Thanks for any information on this.

Joe

-- 
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/