Jean, The deep ground boundary condition is a user input. You may specify either a constant temperature or a zero heat flux condition. Best practice is to specify a constant temperature equal to the average annual air temperature at the depth of either the water table, or 30 meters…whichever is closer to the slab. Regarding the slab thickness, the input SLABDEPTH shouldn’t have any restriction. In fact, often times, depending on the material properties of the slab, the finite difference program will have to increase the thickness of the slab to ensure a computationally stable solution. I have seen some pretty thick slabs in the program much thicker than 25 inches. Hope that helps. Neal Kruis From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jean marais Where does it take its deep ground temperatures from? the weather file? __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.