[EnergyPlus_Support] Boiler loop problems



Dear Forum,
I think I figured this out sometime ago, but have forgotten what I did?..
?	I have a PlantLoop with 2 boiler and a Bypass on the Supply side.
?	I am using "CommonPipeSimulation" in my PlantLoop definition in order to incorporate a secondary / demand side pump.
?	E+ does not like supply side variable speed pumps when CommonPipe is used, so I am using a constant speed pump (P1) on the supply side inlet branch.
?	B1 and B2 do not run continuously.  B1 runs most of the time and B2 operates only when B1 cannot carry the load.
?	Since P1 runs continuously at constant speed, the water temperature leaving the Supply Outlet is diluted ? it's a blend of the B1 outlet temperature and the remainder of the flow, which goes through the bypass.
?	I don't want diluted outlet temperature!  (It's degrading coil performance on the demand side)

Suggestions, please! 
p.s., If I get that part solved, the next step is to figure out how to make P1's power vary with flow.




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/