[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Boiler Loop Problems





Jim,

With a setpoint manager on the supply outlet, you should be getting a constant loop outlet temp.  It's the supply inlet temp that will vary.

Regarding variable pumping - I'm not that familiar with the primary/secondary loop in EnergyPlus.  Another way to approach it is to actually use two plantloops and connect them through a water to water heat pump with COPs in the thousands.  This might give you a little more flexibility.

--
Karen

On Sat, Apr 28, 2012 at 7:20 AM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 

Karen,

The setpoint manager is on the outlet of the supply loop, as you suggest.

..and with a constant speed pump serving both boilers, I agree that the loop temp will vary.

Perhaps my real problem is this:

·         In the real system, there is one (primary) pump per boiler and a VSD pump on the secondary side

·         How do I model that or make an equivalent?

·         And thus get constant loop outlet temps?

 

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Karen Walkerman
Sent: Saturday, April 28, 2012 6:28 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Boiler Loop Problems

 

 

Where is your setpoint manager located? You should be able to maintain a constant temperature on the supply outlet branch. At constant flow, this means that your loop temperature differential will vary.

--
Karen

On Friday, April 27, 2012, jvd2pe <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
>  
>
> Dear Forum,
> I think I figured this out sometime ago, but have forgotten what I did?..
> ? I have a PlantLoop with 2 boilers and a Bypass
> ? I am using "CommonPipeSimulation" in my PlantLoop definition in order to incorporate a secondary / demand side pump.
> ? E+ does not like supply side variable speed pumps when CommonPipe is used, so I am using a constant speed pump (P1) on the inlet branch.
> ? B1 and B2 do not run continuously. B1 runs most of the time and B2 operates only when B1 cannot carry the load.
> ? Since P1 runs continuously at constant speed, the water temperature leaving the Supply Outlet is diluted ? it's a blend of the B1 outlet temperature and the remainder of the flow, which goes through the bypass.
> ? I don't want diluted outlet temperature! (It's degrading coil performance on the demand side)
>
> Suggestions, please!
> p.s., If I get that part solved, the next step is to figure out how to make P1's power vary with flow.
> p.p.s., I tried to send this twice previously, but it has not shown up, so I'm trying again....
>
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___