Dear Forum,
I think I figured this out sometime ago, but have forgotten what I did?..
? I have a PlantLoop with 2 boilers and a Bypass
? I am using "CommonPipeSimulation" in my PlantLoop definition in order to incorporate a secondary / demand side pump.
? E+ does not like supply side variable speed pumps when CommonPipe is used, so I am using a constant speed pump (P1) on the inlet branch.
? B1 and B2 do not run continuously. B1 runs most of the time and B2 operates only when B1 cannot carry the load.
? Since P1 runs continuously at constant speed, the water temperature leaving the Supply Outlet is diluted ? it's a blend of the B1 outlet temperature and the remainder of the flow, which goes through the bypass.
? I don't want diluted outlet temperature! (It's degrading coil performance on the demand side)
Suggestions, please!
p.s., If I get that part solved, the next step is to figure out how to make P1's power vary with flow.
p.p.s., I tried to send this twice previously, but it has not shown up, so I'm trying again....
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/