[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] AHU air temperature control





Thank you for your kind explanation.

 

Best Regards,

Deuk-Woo Kim

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Richard Raustad
Sent: Tuesday, May 01, 2012 9:04 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] AHU air temperature control

 

For the heating SP manager, it looks at the heating load and using the previous zone supply air mass flow rate, calculates a supply air temperature to meet that load. If there is no heating load, the SP is set very low. for the cooling SP manager, same thing happens, but if there is no cooling load, the SP is set very high. These SP's should be placed at different nodes so they do not get overwritten. And note that there is a mixed air SP manager that accounts for fan heat. Use this SP manager to place a SP at each coil outlet node so the resulting supply air temperature exactly meets the zone load (including fan heat).

On 4/30/2012 9:54 PM,
김덕우 wrote:

Dear Richard,

 

Your suggestion is very helpful !

I used SetpointManager:Multizone:Heating object (due to multi-zones) at fan outlet air node of AHU, and the results shows that I really want it.

The discharged air temperature was varied from 16 deg to 35 deg. according to the zone load profile.

 

 

Anyway,

 

It was found that the capability of the SetpointManager:Multizone:Heating object also worked fine in summer design day.

I don’t know why E+ separate SetpointManager:Multizone:Heating and SetpointManager:Multizone:Cooling objects.

Could you please let me know the differences?

 

Best Regards, 

Deuk-Woo Kim 



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
 
UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___