Re: [EnergyPlus_Support] Elegant Solution for AHU heating outlet temp 38 cooling outlet temp 16



EMS can override a node set point.

On 5/2/2012 7:08 AM, Jean marais wrote:
> Dear Group,
> After finding some spar time I've implemented an idea I had a while ago, with some success.
>
> There is a delema of setting a setpoint on a node which is in turn referenced by SetpointManager:MixedAir (used to take into account the fan heat) for an AHU where one wants 16 deg C supply air temp in cooling but 38 degC supply air temp in heating.
>
> The problem was choosing between the SetpointManager:(Multi/Singlezone):Cooling or SetpointManager:(Multi/Singlezone):Heating.
>
> To solve this, I added an extra piece of Object Duct, so that I could place the SetpointManager:(Multi/Singlezone):Cooling on the duct entrance node and SetpointManager:(Multi/Singlezone):Heating on the duct exit node (SupplySide last node).
>
> Then I have SetpointManager:MixedAir objects for the cooling coil (which references the duct entrance Setpoint) and the heating coil (which references the duct exit Setpoint).
>
> The only remaining imperfection is the SetpointManager:MixedAir for my mixing box...it can only reference either for the heating case or the cooling case.
>
> Any ideas?
>
>
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/