Dear Group,
After finding some spar time I've implemented an idea I had a while ago, with some success.

There is a delema of setting a setpoint on a node which is in turn referenced by SetpointManager:MixedAir (used to take into account the fan heat) for an AHU where one wants 16 deg C supply air temp in cooling but 38 degC supply air temp in heating.

The problem was choosing between the SetpointManager:(Multi/Singlezone):Cooling or SetpointManager:(Multi/Singlezone):Heating.

To solve this, I added an extra piece of Object Duct, so that I could place the SetpointManager:(Multi/Singlezone):Cooling on the duct entrance node and SetpointManager:(Multi/Singlezone):Heating on the duct exit node (SupplySide last node).

Then I have SetpointManager:MixedAir objects for the cooling coil (which references the duct entrance Setpoint) and the heating coil (which references the duct exit Setpoint).

The only remaining imperfection is the SetpointManager:MixedAir for my mixing box...it can only reference either for the heating case or the cooling case.

Any ideas?





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/