Roza, The pressure coefficients don't vary with wind speed but they do vary with wind direction. You should make sure you have reasonable values for each direction for which there is significant wind. See the description of AirflowNetwork:MultiZone:ExternalNode, AirflowNetwork:Multizone:WindPressureCoefficientArray and AirflowNetwork:MultiZone:WindPressureCoefficientValues in the Input Output Reference manual You need at least one ExternalNode object and WindPressureCoefficientValues object for each facade that has openings. The pressure coefficients vary across the facade so you may want to have several ExternalNode objects on each facade. You can start with one per facade and add more as your design develops. For further information, consult the AirflowNetwork Model section of the Engineering Reference manual. Phil On 5/5/2012 7:31 AM, roza wrote:
-- ______________________________________________________________________ Philip Haves Leader, Simulation Research Group Lawrence Berkeley National Laboratory One Cyclotron Road, MS 90R3111 Berkeley, CA 94720-8134 (510) 486 6512 (office) (510) 486 4089 (fax) __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |