RE: [EnergyPlus_Support] DOE Reference Building, Elementary School, Chicago problem with NoEconomizer uni




·         Minimum outdoor air flow will not reduce to prevent freezing.  You must define the minimum flow using the Controller: OutdoorAir or other outdoor air object (e.g., DesignSpecification:OutdoorAir)

·         If there is no economizer, the only means of cooling will be the DX coil. 

·         If you have allowed the coil to be available in the cold weather and there is a cooling demand (in a core area, for example), the DX coil will ?operate?

·         E+ provides a warning to alert you, not to say that it is impossible or wrong, since certain DX systems are designed to operate during very cold weather. 

·         In your case, it looks unusual for the coil outlet temperature to be -4C.  Perhaps there is a fairly large minimum outdoor air flow which causes the mixed air / coil entering  temperature to be very low?


__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=24955/stime=1337191321>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmYTR1amVzBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMzcxOTEzMjE->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkaHVucHVkBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzM3MTkxMzIx>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___