Thanks Jim for your message.
1. Yes, Min OA Flow is set by  DesignSpecification:OutdoorAir 
2. Yes, this is a No Economizer zone, with all the consequences
3.  Can I set the threshold or a flag to suppress  the alert? The air temp indeed drops below freezing, and that's the way the Reference Buildings were designed.
4. Yes, the temperature is indeed, due to the cold OA. The coil does not provide any further cooling. The large Min OA requirement is because this unit is serving a kitchen
5. I don't think I need to modify the performance curves, since the unit itself is off during cold weather.

Thanks for your help.

Homero

On Wed, May 16, 2012 at 1:01 PM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 

·         Minimum outdoor air flow will not reduce to prevent freezing.  You must define the minimum flow using the Controller: OutdoorAir or other outdoor air object (e.g., DesignSpecification:OutdoorAir)

·         If there is no economizer, the only means of cooling will be the DX coil. 

·         If you have allowed the coil to be available in the cold weather and there is a cooling demand (in a core area, for example), the DX coil will ?operate?

·         E+ provides a warning to alert you, not to say that it is impossible or wrong, since certain DX systems are designed to operate during very cold weather. 

·         In your case, it looks unusual for the coil outlet temperature to be -4C.  Perhaps there is a fairly large minimum outdoor air flow which causes the mixed air / coil entering  temperature to be very low?

·         If operation of the DX coil is supposed to occur, you may ignore those warnings, but may want to adjust the part load curves to reflect performance during cold weather.

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of hnoboam
Sent: Wednesday, May 16, 2012 12:17 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] DOE Reference Building, Elementary School, Chicago problem with NoEconomizer uni

 

 

I am running the Elementary School, Chicago model from the DOE Reference buildings (after converting to E+7). When I run it, E+ reports 12K warnings, mostly repeats of these two:
** Warning ** Coil:Cooling:DX:SingleSpeed "PSZ-AC_2:5_COOLC DXCOIL" - Air-cooled condenser inlet dry-bulb temperature below 0 C. Outdoor dry-bulb temperature = -10.00
** ~~~ ** ... Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 01/01 07:52 - 07:54

** Warning ** Coil:Cooling:DX:SingleSpeed "PSZ-AC_2:5_COOLC DXCOIL" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = -3.99 C.
** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 01/01 07:52 - 07:54

The economizer type is "NoEconomizer".

Why the Controller does not limit the OA flow to prevent the coil from freezing?

What is the model missing?

I posted the file, in the file section of our group as: ES_Chicago.idf .
Thanks for any help




--
Homero Noboa, Ph. D.



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___